Outside Air - Mobile Home; Mobile Home - Timberwolf T2250 Instructions D'installation Et D'opération

Table des Matières

Publicité

Les langues disponibles

Les langues disponibles

3.4.1 OUTSIDE AIR - MOBILE HOME

Connection from the stove's air intake to outside air is mandatory in mobile
homes only, through a hole in the wall to line up with the knockout in the
pedestal back. Use a fresh air kit. Secure the 4 inch (101.6 mm) diameter
aluminum liner by fl aring the end once it is inserted through the 4-1/2 inch
(114.3 mm) diameter hole in the back of the pedestal. Avoid cutting away wall
studs, electrical wires or plumbing. Seal around the outside pipe with
insulation to prevent drafts.
Attach the rear knockout plate (located inside the ash pan for shipping purposes).
3.5

MOBILE HOME

THE STRUCTURAL INTEGRITY OF THE MOBILE HOME FLOOR, WALL AND CEILING/ROOF MUST BE
THE APPLIANCE MUST BE PROVIDED WITH OUTSIDE COMBUSTION AIR.
USE A CHIMNEY CERTIFIED FOR WOOD BURNING UL 103 S629, TYPE HT (2100°F).
Model T2250 is approved for installation in mobile
homes in the United States only.
The pedestal base must be fi rmly bolted to the fl oor
with 1/4 inch lag bolts. For specifi c clearances, see
"MINIMUM CLEARANCES TO COMBUSTIBLES"
section.
The appliance must be installed between ceiling
joists, with radiation shield and roof fl ashing, so that
the structural strength, insulation and waterproof
qualities of the home are not lessened. Seal with
silicone to maintain a vapour barrier at the chimney
and outside air pipe penetrations.
WARNING
!
DO NOT INSTALL IN SLEEPING ROOM.
MAINTAINED.
THE APPLIANCE MUST BE BOLTED TO THE FLOOR.
INSTALL ACCORDING TO 24 CFR, PART 3280 (HUD).
KNOCKOUT
RAIN CAP
MOBILE HOME
ROOF FLASHING
RADIATION SHIELD
CEILING SUPPORT
TRIM COLLAR
APPLIANCE
BOLTED TO FLOOR
HEARTH PAD
OUTSIDE AIR CONNECTION
THROUGH WALL
47
PLATE
REMOVE TO
ALLOW FOR
TRANSPORATION
W415-1212 / 05.13.13
EN

Publicité

Chapitres

Table des Matières
loading

Table des Matières